0 members (), 560 guests, and 20 robots.
<img border="0" src=&q...uot;300" height="400">
<font face="Arial" size="2">Click Photo for a closer look</font>
Three phase main lug only panelboard is fed from a single phase service
panelboard 30 ft. away. A 100 Amp. three pole breaker in the single
phase
panelboard is protecting feeder conductors and sub panel.
Frank Cinker
Pittsburgh, PA.
So..would this be the infamous "Delta Breaker" in 384-16-f ?
Sparky,
You are correct. I presented this code violation in a previous post. (Code Forum) I thought I would send a photo of the sub-panel. As you can see at a glance, it looks perfectly legal. (Without taking voltage readings) Once the Inspector had the service panelboard cover removed the code violation was quite obvious.
Frank (cinkerf)
Frank;
The Delta breaker deal has been, to my knowledge, a no-no for 2 or 3 decades.
There is confusion as to how the introdution of a third leg ( or in this case 2-A legs, 1-B leg ) was accomplished, simply because nobody is going to advertise this .
This makes it something of a curious oddity to newer trade members as I , who have really only been seriously involved at it since the mid-80's
Perhaps you could give us a little history thread on this sometime here?
PS- I wonder if that 2-pole GFI would work on A+A phase ??
[This message has been edited by sparky (edited 02-19-2001).]
Sparky,
Frank said that a 3pole 100a breaker was in the singlephase panel that fed this. That's where the 3 wires come from - ABA or BAB sequence I would assume.
Sparky go to electricalzone.com click on
article search and type delta breaker.If I can think of any more references I will keep you posted.
http://www.electricalzone.com/archive/search_display.asp?ID=19970201ecm
Delta breaker article, worth reading, thanks Rain
Thanks Bill
This Delta deal is a well thought, but dangerous arangement