#106906 01/24/01 09:39 PM
Joined: Oct 2000
Posts: 3,682
Likes: 3
Admin Offline OP
Administrator
Member
<img border="0" src=&q...uot;400" height="300">
<p align="left">Click on Photo for a closer look

<font color="#000000">Found this at a local gas station. This feeds the HID lighting for the fuel island. </font> <font color="#000000">A B-Cap is just visible, upside down and full of water, connected to the white wires. The black wire has a bare end that may have been fastened to the missing plate's screw, I guess it's the ground. Thought you Hazardous Location guys would appreciate this...

</font>

Virgil Kelly (sparky66wv)

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#106907 01/25/01 09:10 PM
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
Virgil,

I Think I've been to this gas station. It is just up the road from the one that had a gasoline dispenser wired with Romex & since the built in switch was broken, had a plain old light switch to start the pump. Ain't electrical work in WV just great?

Tom


Few things are harder to put up with than the annoyance of a good example.
#106908 01/28/01 02:07 PM
Joined: Oct 2000
Posts: 4,116
Likes: 4
Member
Tom,

Got Pictures?
That would be a good one!


Bill
#106909 01/28/01 03:24 PM
Joined: Oct 2000
Posts: 5,392
S
Member
Good pix 66'....it just looks like a regular jake too, not a class location one

#106910 01/29/01 09:23 PM
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
The dispenser I mentioned was taken out of service after I pointed out the hazards to the owner. The installer of the dispenser (a gasoline wholesaler) felt theere was nothing wrong since he hasn't had any explosions, yet.

I've finally started carrying a camera around. Maybe if I make enough $$$ this year, I'll get a digital one.I do a lot of service calls & inspections so I get to see some real dandy work.

Tom


Few things are harder to put up with than the annoyance of a good example.
#106911 01/29/01 10:05 PM
Joined: Oct 2000
Posts: 5,392
S
Member
Hey, it's the same where ever you go,

Up here i went to a gas station call, self serve, the kid at the counter informed me people were getting "bit" from the nozzle

I got 33 volts to ground [Linked Image]

taking the lower skins off, i found that when the pump had been replaced, none of the fitting were made up, and there was no ground wire

BUT...that station still holds a golden "explosion free" record... [Linked Image]

#106912 01/29/01 10:50 PM
Joined: Nov 2000
Posts: 2,236
Likes: 1
Member
Hey Tom, between us, with help from our location and "mining electricians" (flame magnet?) we should be able to keep as many violation photos up as Bill and Joe!


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
#106913 01/30/01 02:51 AM
Joined: Oct 2000
Posts: 4,116
Likes: 4
Member
sounds like a challenge ...


Bill
#106914 01/30/01 11:40 AM
Joined: Nov 2000
Posts: 2,148
R
Member
Sparky,
re: your post of 1/28/01
I don't think the area in question would be Class 1 Division 1, I think it is Division 2 and if so the fitting in question would be ok for the area(if it didn't have splices and had a cover).
Don(resqcapt19)


Don(resqcapt19)
#106915 01/30/01 07:29 PM
Joined: Oct 2000
Posts: 5,392
S
Member
Don;
I took it as being behind a pump on the island....

#106916 01/30/01 08:04 PM
Joined: Nov 2000
Posts: 2,236
Likes: 1
Member
The conduit and jake are connected to the pillar that holds the canopy. The box to the left is a trash can, but the pumps are within 3 ft. of this area.


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
#106917 01/30/01 08:45 PM
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
'66 & Bill

I guess it does sound like a challenge. I don't think I could afford to take pictures of all that I see. I absolutely have to get a digital camera.

Just so folks don't get a totally skewed idea about coal mine electricians. I wouldn't want their job. When they work underground, they are usually in total compliance with all state & federal mine electrical laws. It's just that they are weak on the NEC when they work aboveground.

By a strange quirk in the mining laws, I hold licenses good for all voltages, all locations. You won't catch me doing underground electrical work. My work would probably be as/more dangerous than what the coal miners do aboveground.


Few things are harder to put up with than the annoyance of a good example.
#106918 01/31/01 12:59 AM
Joined: Oct 2000
Posts: 4,116
Likes: 4
Member
Tom,

I think the same is true in a lot of aspects of our trade. When going to trade school befor getting my license I was in class with experienced utility workers that worked with 13kv and more every day, but had no idea how to do anything inside the building.

By the way, if you should get a digital camera, don't try and go too cheap, do not get anything less than 1 megapixels resolution.

Bill


Bill
#106919 01/31/01 09:23 AM
Joined: Nov 2000
Posts: 2,148
R
Member
Sparky,
The only Div 1 areas are inside the pump cabinet and pits or other below grade areas. The area in question is Div 2 and Div 2 does not require explosionproof fittings.
Don(resqcapt19)


Don(resqcapt19)
#106920 01/31/01 09:10 PM
Joined: Oct 2000
Posts: 5,392
S
Member
Don,this may be but......reading 501-5 section c , class 1 div 1 & 2 goes on about seals etc...
so the reality is if there is a seal, and your piping up the job, the Class 1, div 1 & 2 area's will probably be treated the same. [Linked Image]

#106921 01/31/01 11:28 PM
Joined: Nov 2000
Posts: 2,148
R
Member
Sparky,
If you are installing explosion proof equipment in a Div 2 area you are losing a lot of money. The seal is permitted on either side of the boundary, so in this case it must be inside the pump as it is not outside(of course that would assume that a seal was actually installed as required). I work at a chemical plant and if my electricians are installing explosion proof fittings in the Div 2 areas, I'll soon go broke. In this case the area in question is Div 2 and there is no requirement to install explosion proof fittings in a Div 2 area. Your reference to 501-5(c) applies to the seals only. The wiring methods are in 501-4(a) for Div 1 and 501-4(b) for Div 2.
Don(resqcapt19)


Don(resqcapt19)
#106922 02/01/01 08:06 AM
Joined: Oct 2000
Posts: 5,392
S
Member
I does say that Don, having done a number of gas stations, i will say that we have installed more explosionproof than required.

We even did up the tank monitors as such, an intrisically safe system!

So in reality, this did cost more than it should have. The problem with doing gas stations in an area of 3 states is that many "powers that be" view the job, not all as savey as you with the NEC.

So it's a small price to pay to keep the peace. [Linked Image]