#106894 01/13/01 08:58 PM
Submitted by Virgil Kelly (aka sparky66wv)
This is of a new J box that's over crowded and hard to get an extension on, though I succeeded with some work"
Stay up to Code with the Latest NEC:
>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep
>> 2020 NEC & Related Reference & Study Guides
#106895 01/14/01 09:51 AM
Looks like that pipe & coupling are in the way there....
#106896 01/15/01 06:43 PM
Tom Offline
I see that there are no box offsets in the EMT. I realize they aren't required, but that is definitely poor workmanship. That looks like type MC cable, if it is, was there a connection from the box to all the equipment grounds?
Few things are harder to put up with than the annoyance of a good example.
#106897 01/15/01 08:12 PM
Yes, there was a grounding conductor in the box (from the panel) that was attached to the MC grounding conductors and pigtailed to the box. This was above a suspended ceiling so I can overlook the lack of offsets. The only error was over-crowding the box. Personally, I don't buy any J-box smaller than a 4"x4"x2-1/8".