ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
UL 508A SPACING
by ale348 - 03/29/24 01:09 AM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (ale348), 302 guests, and 14 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#106871 11/13/00 10:06 PM
Joined: Oct 2000
Posts: 3,682
Likes: 3
Admin Offline OP
Administrator
Member
<p align="center">
<img border="0&quo...avid Lewis, Corpus Christi, TX">
<font size="2" color="#FF6898">

</font>Click Photo for Larger Picture

Submitted by: David Lewis,

Electrical Inspector, Corpus Christi, Texas
<p align="left">This box is located on a busy street in front of a commercial strip. It is stubbed up at the grassy area between the parking lot and the concrete sidewalk. We are working to identify the property owner/responsible parties, so that they can be given Notice, to make replacement and repairs of this box. The use of the nonmetallic sheathed cable in the conduit, is not the least of violations which will be listed on the Notice.
<p align="left">Thanks

DavidL.

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Dec 2000
Posts: 27
G
Member
What Article states you can not put NM cable in PVC. Article 336-6 says you must protect NM cable from damage and one of the means is schedule 80 PVC. Article 347 on PVC has no mention of not using it to protect NM cable. I know of Article 400-8(6) that says you cannot run cord in a raceway (except as otherwise permitted in the code, but it provides no hint of where that is.)

Dave T.

Joined: Dec 2000
Posts: 4,294
Member
Although they might be discolored from weathering (a bad situation in itself), it appears that there are 1 black, 2 white, and a green conductor in the homerun. So, why did they culprit feel it was necessary to put white phase tape on that green wire?

[This message has been edited by electure (edited 12-29-2000).]

Joined: Oct 2000
Posts: 4,116
Likes: 4
Member
Good point Electure!

Something doesn't look right with those colors of wires. [Linked Image]