#106303 05/02/05 10:01 PM
This pic goes into the category of things you just know are wrong....but where is code violated?
What you see is a duplex receptacle mounted in a 3-0 box. It is attached where the box cover usually attaches. There are covers made for this box that hold a single receptacle, but not a duplex. An oversize receptacle coverplate will just about cover the front of the box.
- renosteinke
#106304 05/03/05 12:23 AM
I just took a duplex just like that out of service today and it had a Raco Dup cover made of stamped steel.
Rob
#106305 05/03/05 12:38 AM
I may have 1 or 2 scenarios to ponder as violations:
<OL TYPE=1>
[*] Is this Outlet Grounded (Box and Receptacle) - via an EGC?
[*] Is there adequate free Conductor length in this Box?
</OL>
And the most obvious: Why no cover? (hee hee [Linked Image] ...)
Scott35
#106306 05/03/05 12:54 AM
F
John :
i did see cover for 3-0 and 4-0 verison have duplex verison but i dont like it not much becasue the older cover only have single screw to hold the repectaile in place the later cover have two screw or three screw to really lock the repetcale in place i know Raco do make it
Merci , Marc
#106307 05/03/05 09:56 AM
You learn something new every day....
I've never seen the duplex cover for the smaller (3-0) box...didn't know there was one. Maybe this is OK after all?
Sierra- sharp eye! You are correct, the old romex has no ground wire.
As for "free conductor" length, that I'm not so sure about; back then there was no such requirement. Conductors often had insulation skinned off them as they passed through the box, and a very short pigtail twisted and soldered in place, then wrapped with tape.
#106308 05/03/05 04:24 PM
Box should be a device box so that the device can be properly installed.
#106309 05/03/05 06:02 PM
Joe,
The manufacturers make covers for duplex recptacles in octgon boxes, so why would this be an improper installation? (assuming that the cover was actually installed)
Don
#106310 05/03/05 06:23 PM
Don:
I am aware of that cover, and I am commenting on this "incorrect" installation.
The receptacle on the round cover is secured to the octagon box using the two 8/32 screws that are used to secure the entire assembly.
The installation here is not correct under any circumstances!
#106311 05/03/05 06:37 PM
I've seen many of these that have the mounting ears/yoke cut off right at the recptacle. The receptacle is held to the cover with the single 6-32 in the center of the cover, while the cover itself is screwed to the box with the usual 8-32s.
#106312 05/03/05 07:03 PM
Here is that cover --- and the proper receptacle is made without a yoke (strap) and the single 6/32 screw is actually a violation since this would be a "cover mounted" receptacle.
