I took this picture from a 1940 building, its a picture of disconnect switch mounted in the ceiling...
Eng. Sid Elahmad
Electrical Engineer
[This message has been edited by Webmaster (edited 06-14-2005).]
Stay up to Code with the Latest NEC:
>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep
>> 2020 NEC & Related Reference & Study Guides
#106151 06/15/05 01:26 AM
The disconnect is not much of a concern, check out the THHN(?) zip-tied out of the conduit from the left!!
I guess the disco violates the idea of readily accessable.
Stupid should be painful.
#106152 06/15/05 04:37 AM
The height looks like a 'bit' over 6' 7", a violation of 404.8(A)
As for it facing down I do not believe that in itself is a violation.
Gotta wonder what is going on, that is a lot of disconnect connected to 1/2".
#106153 06/15/05 08:59 AM
Is it adjacent to the equipment it supplies? 240.24(A)(4), 404.8(A), exception 2.
Ryan Jackson,
Salt Lake City
#106154 06/15/05 01:22 PM
mxslick: oh and also the fact that the wires are entering that pipe without any protection from sharp edges?
#106155 06/16/05 07:13 PM
K
Missing KO on the disconnect.
Is that a 4/0 cover on a 3/0 box? Appears to be a screw missing there.
#106156 06/16/05 07:30 PM
The wiring coming out of the conduit looks like coax and low voltage cabling.. possibly telephone or network, or CCTV.