(submitted via Joe Tedesco) The conductor cross under an I-beam and enter a box by passing between the edge of the box and the porcelain lamp holder. Violations?:
250.119 ... conductors with insulation or individual covering that is green ... shall not be used for ungrounded or grounded circuit conductors.
300.3(A) single conductors specified in table 310-13 shall only be installed where part of a recognized wiring method of chapter 3
300.20(B) Where a single conductor carrying alternating current passes through metaql with magnetic properties, the inductive effect shall be minimized by ... passing all the conductors in the circuit an insulating wall sufficiently laqrge for all the conductors of the circuit.
404.9 Faceplates provided for snap switches mounted in boxes and other enclosures shall be installed so as to completely cover the opening ....
404.12 Grounding of enclosures Metal enclosures for switches or circuit breaakers shall be grounded as specified in Article 250.
/s/ Jim Williams
|
|
|
|
Joined: Apr 2003
Posts: 60
Member
|
Somebody bothered to penetrate the box twice for this?! And the staples are a nice touch, makes you wonder how it is scorched at the staple above the box if there is only a single conductor there.
|
|
|
|
Joined: Dec 2004
Posts: 161
Member
|
Not enough respect for electrics your side of the pond, 110 volts is just too easy. One belt from the 240 volts everywhere here is enough to stop this kind of thing.
|
|
|
|
Joined: Mar 2004
Posts: 391
Member
|
I sure do love the arts-'n'-crafts staples. I've seen telco and cable wire attached to people's walls that way by the hired "proffessional contractors" from the local cable company. -John
|
|
|
|
Joined: Nov 2002
Posts: 794 Likes: 3
Member
|
300.20(B) Where a single conductor carrying alternating current passes through metaql with magnetic properties, the inductive effect shall be minimized by ... passing all the conductors in the circuit an insulating wall sufficiently laqrge for all the conductors of the circuit. Don't "knob and tube" methods violate this rule? Each wire, in loom, enters a box in its own hole, yes? In any event, it looks like whoever did this had once seen "knob and tube" described in some book, and made a "scientific wild ass guess" (SWAG) based on that with this install.
|
|
|
|
Joined: Jul 2002
Posts: 717
Member
|
What is the fuss, he used a commercial grade switch!
|
|
|
|
Joined: Dec 2000
Posts: 4,294
Member
|
IM{not so}HO, I doubt that any of the Code references cited here would apply.
Don't get me wrong, this this installation is way wrong, and always was.
The point I'd like to make is that the Code changes each cycle, and work that's old was not installed according to future Codes. (For example, old boxes weren't necessarily required to be grounded)
The drawn handy box, the use of TW or THW wire, and the old switch hint to me that this has been there a long time (the wood above the door frame looks fairly new)
Sorry to use such a hack installation to illustrate my point.
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
Who are you and what did you do with electure!
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Dec 2000
Posts: 4,294
Member
|
Aww, Bob, It's really me I just get a kick when I see somebody applying 2002 Code references to a 1950's installation. An example: I just looked at a little "upgrade" job; providing GFI protection for the underwater light on a 1957 swimming pool. It has been untouched except for lamp replacements since then, and still has the "grillework" across the front that was (I think) required back then. GFI wasn't Someone quoting the 2005 Code would have a field day with it Fear not, I'm still just as grumpy an old man and extremely opposed to Code violations and unsafe practices as ever.
|
|
|
|
Joined: Sep 2002
Posts: 943 Likes: 2
Member
|
One thought, could this been a job useing "recycled" materials?IMO if so, would have been better to go to a recycler.
|
|
|
Posts: 8,443