Joined: Aug 2001
Posts: 7,520
P
Member
Quote
I'm not sure if that top black is a conductor, or a uncut ty-wrap..
I think it's the latter. In fact it looks as though we might be seeing the uncut ends from two - one on the bundle of red wires above and one from a bundle on the right.

[Linked Image]


P.S. The phase colors have been bugging me, and thinking about it some more I seem to recall our esteemed Webmaster telling us once that red-black-blue ordering is also common in Long Island.

Bill, are you out there? Am I imagining things? [Linked Image]



[This message has been edited by pauluk (edited 06-29-2005).]

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Aug 2004
Posts: 51
B
Member
Are some of the conductors passing from the vertical conduit(s) through the first panel, and into the second one?

Perhaps even passing through to somewhere else? Would this be forbidden?

Joined: Nov 2001
Posts: 42
A
Member
I AM AN ELECTRICIAN ON LONG ISLAND...THE COLORS FOR A 3 PHASE WYE CONNECTED SERVICE ARE BLUE-BLACK-RED AS PER LIPA..


JBIELECTRIC EAST MEADOW NY
Joined: Aug 2005
Posts: 89
D
Member
Wouldn't that cause a field around the conduits, cause them to chatter and fluctuate, and then turn cherry red hot?

Joined: Dec 2000
Posts: 4,294
Member
My guess is that there probably is a wireway above these panels.
Not only would you have the violation(s) you can see here, but the wireway above would probably have more than 100 conductors in a cross-section, not derated.
This is a "pet peeve" of mine, and I see it too often.
"Elektrition" will put as many 3/4" or 1" conduits across the top of the panel as will fit, so they don't have to figure anything out. (Note the empty conduits) [Linked Image]

Joined: Aug 2005
Posts: 89
D
Member
I've seen empty conduits before, at a new construction at my university. My electrical teacher said that it's fine to do that, plus easier on the rough-in, and have them meet at a junction box, just in case you'll even need to pull a new circuit to a new location.

Joined: Oct 2000
Posts: 2,749
Member
[Linked Image]

On a recent walk-thru I noticed the EC didn’t run separate hot, neutrals, and grounds for circuits that I indicated on my drawings.
I told the EC he needed to go back and add dedicated neutrals and grounds for the circuits indicated. This was his solution.

I questioned them about the code violation, said they never heard of that in the code.

By the way, this was the owner of the company and his lead foreman.

Craig Lusinger


Joe Tedesco, NEC Consultant
Joined: Dec 2000
Posts: 4,294
Member
I'd like to see the Code reference for the "dedicated neutrals" myself.
Isn't "dedicated neutral" an oxymoron? If the grounded conductor is a dedicated one, then it's not a neutral, is it?

Nonetheless, if it was on the drawings, and part of the contract documents, they should have done the job per specifications.

Joined: Oct 2000
Posts: 2,749
Member
Morning Electure:

Get that first cup of coffee, you will be busy today, I have some great shots and stories for you!


Joe Tedesco, NEC Consultant