AHJ is "Authority Having Jurisdiction", which is the inspector or building official.

steve


Steve
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Dec 2000
Posts: 4,294
Member
AHJ= Authority Having Jurisdiction.

If this was a commercial electrician's job, he is no doubt violating the Code with his gutter installations everywhere he goes.
If there are more than 30 current carrying conductors in any cross-section of a metallic gutter or wireway, they must be derated per ('02) 310.15(B)(2)(a).
See 366.7(A) and 376.22


Sure, it probably passed [Linked Image]