CODE VIOLATIONS What’s Wrong Here? By Joe Tedesco, NEC Columnist How well do you know the Code? Think you can spot violations the original installer either ignored or couldn’t identify himself? Here’s your chance to moonlight as an electrical inspector and second-guess someone else’s work from the safety of your living room or office. Joe Tedesco, who has a knack for finding shoddy electrical work, did the dirty work and found this mess. Now it’s your turn to identify the violation.
Joe Tedesco, NEC Consultant
|
|
|
|
Joined: Apr 2004
Posts: 28
Member
|
Well the pipe should be reemed and then we need a fitting with some type of bushing.And with the looks of the conduit it might be a little tight for both of them.
|
|
|
|
Joined: Apr 2002
Posts: 7,383 Likes: 7
Member
|
Joe: A one word "What's wrong" would be EVERYTHING! Conduit not reamed No connector or threads/locknuts/bushing. Excessive cable jacket within the "enclosure" Cable installed in conduit?? (No from-to) NO bonding of the conduit. The 'remains' of the hole, hanging in the enclosure. And there must be a lot more that is out of the range of your lens. BTW, what ssize is the 'enclosure?? ..
John
John
|
|
|
|
Joined: Jun 2003
Posts: 681
Member
|
What code violation is "excessive cable jacket" inside the enclosure? 300.10 300.15 There is a possible pipe fill violation.
Pierre
Pierre Belarge
|
|
|
|
Joined: Oct 2000
Posts: 2,749
OP
Member
|
Please continue .....
Joe Tedesco, NEC Consultant
|
|
|
|
Joined: Apr 2004
Posts: 28
Member
|
Well there is definity some problems here. 1.Subpanel grounds and neutrals comebined. 2.Extra set of wires in the lugs with feeders going somewere without over current protection. 3.White wire on breaker. 4.Freeder Neutral not reidentified as white. 5.Loose connection on lugs panel buned up needs replacement. 6.I hope they derated all them wires in that conduit.
|
|
|
|
Joined: Dec 2004
Posts: 161
Member
|
Insulation overstripped on a couple of wires?
Can't see it too well but what's going on in the top left corner with the knock-out possibly left open and no grommit?
|
|
|
|
Joined: Nov 2002
Posts: 134
Member
|
What the heck is this panel? Federal nonsPacific???
I'm just a youngin' I've only ever seen Square D, CH, ITE, GE, Siemens.... this is new to me....or old...as the case may be.
RSlater, RSMike
|
|
|
|
Joined: Oct 2004
Posts: 806
Member
|
RSmike: That lovely panel is our old friend, Zinsco. Popular here in So Calif. along with FPE and Pushmatic.
Stupid should be painful.
|
|
|
|
Joined: Nov 2003
Posts: 16
Member
|
I'm guessing this is actually a main service panel with NO MAIN breaker. Zinsco or Sylvania. I looked again. It is a main service panel. The top 2 lugs are for the service entrance, while the 2p70 is the "lighting main" for the lower half of the panel. The top 2 pole breaker is "legal" but the 1/2 breakers in the center are not.