Joined: Oct 2000
Posts: 2,749
Member
[Linked Image from nachi.org]

The Inspector said:

"Fortunately, they were old nests. He couldn't figure out how they got into the panel. There were no missing knockouts, or any openings that he could see."


Joe Tedesco, NEC Consultant
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Feb 2004
Posts: 1,438
Member
You'd be amazed where the wasps can fit in... I've come across these a couple times as well.... Panel cover not flush with the can or wall?

-Randy

PS.. Ckt 11 needs reidentified, there appears to be a black conductor on the ground bar, & why is there a stripped, loose conductor towards the top above the mudnest on the phase? [Linked Image]

Joined: May 2004
Posts: 697
D
Member
This brings me to one of my unanswered questions in electrical life.

I've read some very good posts on arranging exterior conduit to drain, then drilling holes in the lower conduit bodies or boxes for drainage (or cutting a small section of the gasket out to drain). My only problem with these solutions is...what size hole will allow drainage (allowing for some corrosion or dirt that might plug the hole), but not allow insects into the system???

Dave

Joined: Nov 2000
Posts: 2,148
R
Member
That looks like a NEMA 3R panel, if so there are drain holes at the bottom that were put there by the panel manufacturer.
Don


Don(resqcapt19)
Joined: Sep 2003
Posts: 123
M
Member
Another good reason for safety glasses. What other PPE do you need? Contact cleaner works wonders on the live ones.

Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
Lucky they weren't live nests. I have been here before! Open the panel.... Put the cover down. Look up into angry hornets bent on destruction.

As for how they got there, they'll squeeze through any opening larger than an 1/8". Like the gap of the panel cover lid, then through the next one. It's like their bodies flatten out to squeeze through.

[This message has been edited by e57 (edited 05-22-2004).]