Not to mention the disconnecting means?LOL!?!?!
Is that 2 pole full space breaker a BR series type breaker also. just curious.
remove and replace
[This message has been edited by wirenut73 (edited 05-25-2004).]
Loadcenter is a common tern used in the field and we understand that, but the term panelboard and cabinet are defined in Article 100. I did not take the picture and called attention to it to address the subject in 110.12(C).
I'd be more concerned with all the three wire circuits that appear to have both wires tied to the same side of the line thereby overloading the neutral in each circuit.
I was going to say maybe the conduit is used for ground but then I saw the post saying about the ground bar. Phew!! [Linked Image]
[This message has been edited by Theelectrikid (edited 09-01-2004).]
It looks like a painted subpanel feeding who knows how many more (possably, sorry, probably) painted sub-panels.
Wait a minute, just noticed something. Is that bottom-right hand two-pole CB rated for aluminum wiring? If it's not, call 9-1-1 for a heads up! But then again, maybe the painter tryed applying gloss to fool us all?????
I see several tandems that each has one black and one red wire on it. I wonder if those are multiwire circuits with badly overloaded neutrals?