In Arizona doesn't seem to withstand the effects of the earth? What does UL have to say about this and does the NEC cover this situation? [This message has been edited by Joe Tedesco (edited 03-07-2005).]
Joe Tedesco, NEC Consultant
|
|
|
|
Joined: Aug 2001
Posts: 7,520
Member
|
That looks bad, especially for a dry climate like Arizona. Or is this the result of galvanic action of some kind?
By the way, what's the usual thickness of the metal used for EMT?
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
Paul, EMT is roughly the same as the exhaust pipe on a car.
Bob
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Nov 2002
Posts: 174
Member
|
EMT wall thickness runs from 0.042 for 1/2 inch to .083 for 4 inch.
Compare that to Rigid Steel which runs from .104 to .225.
BTW IMC runs from .070 to .140.
|
|
|
|
Joined: Aug 2001
Posts: 7,520
Member
|
Thanks. There was some thinwall conduit used in the U.K. in the past, but nowadays we don't really have an equivalent to EMT in general work, just PVC or heavy-gauge steel.
|
|
|
|
Joined: Aug 2002
Posts: 1,081
Member
|
ARTICLE 358 Electrical Metallic Tubing: Type EMT
358.10 Uses Permitted. ... (B) Corrosion Protection. Ferrous or nonferrous EMT, elbows, couplings, and fittings shall be permitted to be installed in concrete, in direct contact with the earth, or in areas subject to severe corrosive influences where protected by corrosion protection and judged suitable for the condition. (C) Wet Locations. All supports, bolts, straps, screws, and so forth shall be of corrosion-resistant materials or protected against corrosion by corrosion-resistant materials.
358.12 Uses Not Permitted. EMT shall not be used under the following conditions: (1) Where, during installation or afterward, it will be subject to severe physical damage (2) Where protected from corrosion solely by enamel ... (6) Where practicable, dissimilar metals in contact anywhere in the system shall be avoided to eliminate the possibility of galvanic action Exception: Aluminum fittings and enclosures shall be permitted to be used with steel EMT where not subject to severe corrosive influences.
|
|
|
|
Joined: Jul 2003
Posts: 394
Member
|
It looks like it may be "lava rock" around those pieces. If so, I have found that lava rock is very corosive, even to galvanized material. I've seen it eat completely through window wells when it was used around the foundation. This may be a location where Suitable for conditions is important.
|
|
|
|
Joined: Oct 2000
Posts: 2,749
OP
Member
|
This picture was taken in Las Vegas last year.
Joe Tedesco, NEC Consultant
|
|
|
|
Joined: Apr 2002
Posts: 197
Member
|
You're just " nitpicking ".
|
|
|
|
Joined: Oct 2000
Posts: 2,749
OP
Member
|
Gwz continued ....
Define "nitpicking"
How in the heck are you! What's up? Did you send in any Proposals, and did they get accepted?
How about Comments?
Joe Tedesco, NEC Consultant
|
|
|
Posts: 57
Joined: August 2003
|
|
|
|