ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 266 guests, and 14 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#104086 12/25/02 09:14 PM
Joined: Oct 2000
Posts: 2,749
Member
[Linked Image]

These wiring methods were buried in the sand on a beach!



[This message has been edited by Joe Tedesco (edited 02-17-2003).]


Joe Tedesco, NEC Consultant
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Apr 2001
Posts: 518
J
Member
Remember Carl, who wanted us to explain the "why" as well as the "what?"
Bell boxes, made of zinc, are quite often not resistant to corrosion where they are located. Both salt spray and direct burial seem to lead to their rapidly corroding away.
The lack of burial depth is not as simple an issue as it would first appear. Would you rather the assembly be beneath the water table?
Near the surface as it is, it is subject to both movement (shifting sand) and mechanical damage (tripping). Either can result in the wires (and connections) being damaged.
Where you have movement, it is important that your connections be made in such a way that any strain is not transmitted to the conductor connections. The use of "smurf tube" makes sure that the strain is absorbed only by the connections- just the opposite of what we want.
Lest I open a whole new can of worms, this MIGHT be a place for SO cord, strain relief fittings, and PVC (NEMA-4X) boxes. It all depends upon what the circuit is derving!
We often chide people for using plumbing components for electrical work- yet I am not aware of any listed bronze or stainless conduit. If I were to pipe this, I'd consider using SS plumbing pipe.
I don't like UF, for a number of reasons. I don't think UF is subjected to a salt-spray test; nor do I think that there are NEMA-4 strain relief fittings for any but the smallest sizes. I'd have to research this before I rule UF out.
If that box is there only as a splice, I would suggest that a resin/epoxy spliceing kit would be preferable to a box. A buried box is not accessible, in any event.

Joined: Oct 2000
Posts: 2,749
Member
Thanks John for your reply. This was an energized circuit that was run to a cabana!


Joe Tedesco, NEC Consultant
Joined: Feb 2003
Posts: 288
Y
Member
"We often chide people for using plumbing components for electrical work- yet I am not aware of any listed bronze or stainless conduit. If I were to pipe this, I'd consider using SS plumbing pipe."

Well, I've seen SS before, in a semiconductor manufacturing plant. I've seen threading dies ruined by people who didn't know they were not for SS. There were condulets that were SS and I think they were chrome plated. I didn't run any of the stuff myself but I remember it had to be laboriously polished before installation (customer rules). I assumed it was Listed but I really don't know for sure.