Joined: Oct 2000
Posts: 2,749
Member
[Linked Image]

Bewildered! Designed by the woodshop supervisor!

The explosion proof switch probably costs more than the saw equipment.


Joe Tedesco, NEC Consultant
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Aug 2002
Posts: 402
J
Member
Sawdust can be an explosion hazard just like grain dust if it is fine enough.

Joined: Oct 2000
Posts: 2,749
Member
True

Quote
Class III locations usually include textile mills that process cotton, rayon, and so on, where easily ignitible fibers or combustible flyings are present in the manufacturing process. Sawmills and other woodworking plants, where sawdust, wood shavings, and combustible fibers or flyings are present, may also become hazardous. If wood flour (dust) is present, the location is a Class II, Group G location, not a Class III location.
www.necdirect.org




[This message has been edited by Joe Tedesco (edited 11-08-2002).]


Joe Tedesco, NEC Consultant
Joined: Oct 2002
Posts: 210
S
Member
Better safe than sorry. But still seems a little extreme.

Joined: Mar 2001
Posts: 2,056
R
Member
There's more to this than meets the eye.
That sure looks like a Class 1, Div.1 disconnect. What about the conduit seal?
What about the NEMA 12 enclosure fed by
sealtite?

Let's play "Guess the Classification"

[This message has been edited by Redsy (edited 11-08-2002).]

Joined: Sep 2001
Posts: 136
S
Member
I thought that saw dust would have fallen into Class II locations. Class I is flammable vapors and gases, Class II is dust, and Class III is Ignitable Fibers and Flyings??? Although wood dust is not exclusively mentioned in the UL classifications, would it not be considered a Class II location. Just asking the elctrical experts.

Bryan www.SAFTENG.net

Joined: Jul 2001
Posts: 599
J
JBD Offline
Member
The simple presence of wood saw dust does not create a Class II hazardous location. If it did all of our circular saws and sanders would need to be dust ignition-proof.

According to Killark's 1999 National Electrical Code Review & Application Guide " To be considered a "dust" the combustible material must exist as a finely divided solid of 420 microns (0.420 mm) or less. Such a dust will pass through a No. 40 U.S. sieve."

Joined: May 2002
Posts: 1,716
R
Member
The dust shouldn't be a problem in this case.

Check out the below floor dust collector.

But look in the background, there's another one of these switches.

BTW, The band saw is mighty high dollar itself.

Roger

Joined: Mar 2002
Posts: 360
T
Member
Are you sure we are looking at just a disconnect?
That gizmo sure looks like a rotary three phase converter to me.
But then I have been known to be wrong, on numerous occasions [Linked Image]

TW

Joined: Mar 2001
Posts: 2,056
R
Member
Roger,
Good eye with the additional disco. Also, above the (non-xp)panel is what appears to me an explosion-proof j-box of similar classification.
Either somone got a deal on surplus or stolen materials, or some contractor sold the owner a line of bull.

[This message has been edited by Redsy (edited 11-11-2002).]