If you are working with fine strand wire such as motor leads, GTF, control wire, then I like to put a compression termination on them. If you twist a marrette on these, you tend to lose a few strands reducing your current carrying capacity. Also 32-100(2) tells us to bunch tin or use compression connectors for more than 7 strand fire alarm conductors.