ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 252 guests, and 20 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#102627 07/07/06 12:12 AM
Joined: Jun 2005
Posts: 17
M
MJ2000 Offline OP
Member
Customer wants to use 12kw standby generator
to feed all house(200 amp service) in case
of blackout.Mostly lights,fridge,plugs,etc.
Does rule 08-104(2) apply for this case?
Thanks

#102628 07/07/06 11:49 AM
Joined: Jun 2006
Posts: 613
M
Member
12 kw is 50 amps at 240 volts so that is the rating of the generator and you can connect 80% of that. If he wants to run the whole house he needs a bigger generator. So what is the solution? Take the most essential loads like the fridge, some lights, any pumps essential to sanitation or flood protection possibly. Add a bit of heat for one room and a few convenience outlets for the wireless phone and a hot plate and you are getting to the limit. The load center must be connected through an approved transfer switch with a source from the regular panel and 1 from the generator. Both sources would have a 50 amp breaker ahead and feed a 60 or 100 amp loadcenter through the transfer switch. The grounding at the generator must be checked to ensure the neutral is not grounded as most transfer switches will have a continuous neutral.

#102629 07/08/06 02:23 PM
Joined: Jun 2005
Posts: 17
M
MJ2000 Offline OP
Member
The problem is if you want to have all lights
in house and possibillity of using all plugs,in this case you need many circuits to put on
subpanel(plus fridge,subpump,furnace etc).
The easiest way is to install main
disconnecter after meter and transfer switch
(service rated) and connect generator. Customer knows that generator is not big enough for all house(full calculated load) and will take control of load. Generator is protected of overload so that I can't see a problem for this solution.
If customer is not at home in case of blackout generator is big enough for load
remain switched on.

#102630 07/26/06 07:14 PM
Joined: Jun 2006
Posts: 613
M
Member
Mj it is still a violation to connect a load greater than the generator capacity so the essential circuits must be seperated from the main service and fed via the transfer switch through a load center to 80% of the max rating of the generator.

#102631 07/26/06 09:52 PM
Joined: Apr 2006
Posts: 31
M
Member
12kw @ 120v is 100 amps, that's all you have so it will not meet the needs of a 200 amp panel. 8-104(2) "the calculated load of a circuit shall not exceed the ampere rating of the circuit".

I think mikesh is correct, you will need a transfer switch and sub panel, I get the impression the owner wants to backfeed the existing panel.