O.K. here's the solution. If I can get it out of my head and onto the keyboard in a way that is understandable to the readership (I don't mean the readership
can't understand, I mean the writer's ability at the keys is limited). I have submitted to the contractor's engineer the following:
The PoCo's overhead transformer bank is on the oposite side of a road from the location of the temporary service that I will be providing. So, I will be building a "rack" out of treated wooden poles 40'X 11" butt diameter, 4'X8' treated plywood, and unistrut. I plan on setting an N3R gutter with a 3" riser containing (4) 500 Kcmil. The service voltage will be 480 volt, 3 phase, wye. The gutter will be tapped with (1) 200/3/200AF disco w/ solid neutral, and (1) 100/3/100AF disco w/ solid neutral. Each disco will feed an HD7 20-53 self contained meter can. The 200 and 100 will feed risers that contain (4) 3/0 and (4) #3 awg respectively. These conductors will splice onto #4/0 and #1 quadraplex via CU/Al rated split bolts, and span some 1,500' via "shorter" treated wooden poles, "strain" hangers, and hardware. At the end of the span the 4/0 quadraplex will drop into a riser containing (4) 3/0 copper conductors which will feed an N3R gutter. The gutter will be tapped with (2) 200/2/175AF Disco's which will each feed a 75 KVA, 480/240-120 Volt transformer, and each of those will feed a single phase, 240/120 volt panel with 300 Amp MCB. One set of job trailers will be fed from these panels. The other quadraplex will feed a 50 KVA, single phase transformer, which will in turn feed a gutter with existing disco's. Ground rods, GEC's, ect. will be used at the service, and at transformers. I hope that all can make sense of this. Your comments may be welcome......depending on how critical you are......
The price tag on this little project will be between 40 and 60K.....ouch!
Sanity after Temporary Insanity,
Doc
P.S.
The jury is still out, on whether I'm sane or not. Because I've got to be crazy for getting involved in this project.