526
20
I was working on a cottage recently, adding a few new circuits for a sump pump and washing machine and cleaning up some one else’s creative wiring.
The cottage has a detached shed, fed by a 3 conductor TEK, the original installer fed the TEK off of the living room lighting circuit, one of the conductors was a supply for the inside lights and plug, another was used as a switch leg so that the outside light on the shed was controlled by a switch in the living room. There is of course a neutral and EGC.
I moved the shed onto its own breaker. I was wondering on what everyone’s thoughts on how I could cover the service disconnect for this shed.
not sure what you mean by "cover the service disconnect for this shed"
Sorry, my poor choice of wording.
I am asking for insight on how you would provide a service disconect for this shed.
You would not really have a service disconnect to an outbuilding,since what you are describing is a branch circuit off your main panel. What you may require, depending on how much power you are bringing to the outbuilding, could be some kind of sub-panel. Be sure to read CEC 10-208. You are allowed two 15 amp circuits to the outbuilding without a subpanel-but I cant find that rule, be sure to talk to your local AHJ to check local rules also.
I would look at this in two ways. If it is a home there would be no requirement for a disconnect at the shed and I might prefer to see a sub panel I cannot think of any reason that a person would be required to run a sub panel and feed the circuits from their. Even a commercial application if the shed is not a seperate tennant then it could still be fed either via a sub panel or separate circuits. Now if the shed was functionally seperate IE a different tennant then a panel with a local disconnect would be in order. In BC each occupancy must have a local disconnect within the occupancy.
In Ontario this rule applies: 14-418 Disconnecting Means
(1) A single disconnecting means shall be provided either integral with or adjacent to the distribution equipment:
(a) Within each unit of a multi-unit building, other than a dwelling unit;
(b) Within each area common to more than one building, such as an underground parking area; or
(c) Within each building when fed from another building.
(2) Subrule (1) does not apply to circuits from part of fire alarm, fire protection and emergency systems.