#102533 - 05/26/06 12:50 PM do I need a neutral conductor?
bigpapa Offline
Member
Registered: 03/18/06
Posts: 77
Loc: canada
I want to extend a feeder from building A to building B.
Building A has a 600/347V Y 3 phase service.
I want to bring 600V 3 wire to the second building and feed a 600V- 120/208V transformer and establish a neutral at the new service. I do not need 347V there.
Is a neutral required in the feeder?
Top
Tools for Electricians:
#102534 - 05/26/06 04:56 PM Re: do I need a neutral conductor?
bigrockk Offline
Member
Registered: 01/25/03
Posts: 174
Loc: Middle of Canada
I believe you do, based on Rule 4-026(b)(19th edition CEC)
Top
#102535 - 05/26/06 08:29 PM Re: do I need a neutral conductor?
jay8 Offline
Member
Registered: 07/28/05
Posts: 183
Loc: Vancouver, BC
You would feed the transformer primary with 600 volt delta, the neutral is the grounded XO point on your secondary. See 10-210.
Top
#102536 - 05/26/06 09:59 PM Re: do I need a neutral conductor?
Check Pilot Offline
Member
Registered: 11/25/05
Posts: 141
Loc: Edmonton Alberta Canada
FYI from the new CEC 20th Edition.

4-026(b) Installation of neutral conductor

Where a service, feeder, or branch circuit requires a neutral conductor, it shall be installed
(a)in all seperately enclosed switches and circuit breakers;
(b)in all centres of distribution associated with the circuit;
(c)with all connections to the neutral being made in the enclosures and centres;and
(d)ins such a manner that any neutral conductor may be disconnected without disconnecting any other neutral conductor.

10-210 Conductor to be grounded

(1) For alternating-current wiring systems, the conductor to be grounded shall be as follows:
(a)single-phase, 2 wire-the identified conductor;
(b)single phase, 3-wire-the identified neutral conductor;
(c)multi-phase systems having one wire common to all phases - the identified neutral conductor;
(d)multi-phase systems having one phase grounded-the identified conductor;
(e)multi-phase systemsin which one phase is used as in Item (b)-the identified conductor.

(2)In any multi-phase system in which one phase is used as a single-phase 3-wire system, only one phase shall be grounded.

Hope that helps. Check your local code that is in effect. - This one is from the new 20th edition - 2006.
Top
#102537 - 05/26/06 11:22 PM Re: do I need a neutral conductor?
bigpapa Offline
Member
Registered: 03/18/06
Posts: 77
Loc: canada
In my case, as I read it, a neutral conductor need only be installed if required
which in this case it isn't.
I see no reason it would be required, and a bonding conductor would suffice to limit any faults.

"Where a service, feeder, or branch circuit requires a neutral conductor, it shall be installed"
Top
#102538 - 05/30/06 07:45 AM Re: do I need a neutral conductor?
bill woods Offline
Member
Registered: 11/21/01
Posts: 45
pretty sure you don't need a neutral. be aware though you do need to bond your new system back to your main in building "A" from the XO in your new service.
Top
#102539 - 06/02/06 09:48 AM Re: do I need a neutral conductor?
Rewired Offline
Member
Registered: 01/01/06
Posts: 558
Loc: Hamilton, Ontario, Canada
I will have to agree that you would not need a neutral... You would need 3 hots and a bond thats it, UNLESS you plan on having 347V lighting... You would bond X0of the transformer to ground, effectively "grounding" the secondary... You would not connect the neutral of the feeder (if you had one) to XO as its a "groundED" conductor, not the
"groundING" conductor....

A.D
Top
#102540 - 06/09/06 10:02 AM Re: do I need a neutral conductor?
mikesh Offline
Member
Registered: 06/07/06
Posts: 613
Loc: Victoria, BC, Canada
Yes you absolutely do have to bring a neutral to the next building regardless of the need for it there.

10-204(2) is the rule you want. The clue here is the 347 volts makes the system derived from a grounded system and you need a neutral or more accurately a grounded circuit conductor for your overcurrent protection
Top
#102541 - 06/09/06 02:27 PM Re: do I need a neutral conductor?
Rewired Offline
Member
Registered: 01/01/06
Posts: 558
Loc: Hamilton, Ontario, Canada
A GroundED or a groundING conductor.. there IS a difference,
What would you connect the neutral to in the new building to anyway?
Top
#102542 - 06/09/06 03:21 PM Re: do I need a neutral conductor?
bill woods Offline
Member
Registered: 11/21/01
Posts: 45
i think if you look at appendix B you will understand the connections better. page 373 of the 20th edition. see where it says source (line side)? imagine that a transformer has been installed along the vertical dotted line at the right side of source between source and service/distribution. on the service/secondary side the neutral is still connected to the transformer XO and from the XO there is a groundING conductor connected back to the main service groundING conductor. thus there is an effective connection to ground thru the ground electrode at the main.
Mikesh i think you might be mistaken about the neutral being needed. if the application is to supply 120/208v to building B all you need is the three phases to transform from 600 down to 208. a connection to the XO derives the 120v. the XO is connected to the system ground thus creating the 120v required. if there is a need for 347v in building B yes a neutral will need to extended from building A.
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
2 registered (gfretwell, sparkyinak), 53 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals