#10222 06/02/02 07:54 AM
Joined: Jul 2001
Posts: 311
F
Member
I believe it would be Code compliant to run one underground branch circuit to a storage shed and install a duplex receptacle without driving a ground rod etc. The single branch circuit would of course include an equipment grounding conductor. Am I correct?

#10223 06/02/02 10:07 AM
Joined: Apr 2001
Posts: 507
G
Member
yes

#10224 06/02/02 12:21 PM
Joined: Nov 2000
Posts: 2,148
R
Member
Frank,
Don't forget that 225.31 requires a disconnect at the shed. The exception to 225.38 permits the use of a "snap" switch as the disconnect.
Don


Don(resqcapt19)
#10225 06/02/02 07:02 PM
Joined: Jul 2001
Posts: 311
F
Member
Thank you for replies. I wasn't aware of the disconnect rule Don. A snap switch is certainly easy enough.