ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 263 guests, and 17 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#101797 05/13/03 04:52 PM
Joined: May 2001
Posts: 378
F
frank Offline OP
Member
Looking for CEC code rules regarding number of wires that can be terminated at a single terminal for breakers,neutal buss bars and grounding bars ect.thanks

#101798 05/13/03 07:29 PM
Joined: May 2001
Posts: 144
T
Moderator
#2-034

Use of Approved Equipment

No one shall use any electrical equipment other than approved electrical equipment of a kind or type and rating approved for the specific purpose for which it is to be employed.

Appendix B

As a condition of approval of certain types of electrical equipment, the manufacturer supplies instructions pertaining to its installation. It is of the utmost importance that the installer closely follow installation instructions supplied by the manufacturer to fulfill the terms of the approval agreement.

Tony Moscioni
Electrical Inspector
Electrical Safety Authority

#101799 05/13/03 07:52 PM
Joined: May 2003
Posts: 1,158
Member
6-212 (1)


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5