The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured Items:

Switch Bit - Interchangeable Flex Bit System
>> Switch Bit -
Interchangeable Flex Bit System

>> 2014 NEC and Related

Recent Posts
Possible to install Schuko outlet in US?
by gfretwell
12/21/14 01:13 PM
Euro outlet in US kitchen
by Meadow
12/20/14 09:55 PM
Looking for a hard to find electrical part
by BigB
12/20/14 07:53 PM
Zip cord for low voltage undercabinet lighting
by BigB
12/20/14 01:52 PM
What % of time working on energized equipment?
by LarryC
12/20/14 01:48 PM
New in the Gallery:
Another find....
Shout Box

Top Posters (30 Days)
gfretwell 23
Meadow 18
renosteinke 17
HotLine1 17
dsk 16
Who's Online
1 registered (gfretwell), 90 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#101748 - 02/23/03 01:29 PM exit sign and emergency light hookup?
RobbieD Offline
Member

Registered: 02/23/03
Posts: 238
Loc: Canada
I am used to installing exit sign/emergency lighting unit combos. This time I must install an exit sign and an emergency light seperatly. Everything will be surface mounted using emt. I will be running emt from the panel to the exit sign and to a receptacle next to the lighting unit.The light unit will be plugged into it. Both will be on the same circuit and there will be nothing else in the conduit. My question is how do I supply the back up power(6VDC) from the emergency light unit to the exit sign? I want it to look nice. I don't think I can run 6Vdc in the same conduit as the 120VAC. Is the exit sign considered a remote device of the lighting unit in this case? If it is can I run the 6VDC in the same Conduit as the 120VAC if all conductors are insulated to the highest voltage rating? If not does anyone have any suggestions on how to wire it so it looks nice? Thanks

Top
2014 / 2011 NEC & Related Books and Study Guides
#101749 - 02/23/03 09:35 PM Re: exit sign and emergency light hookup?
ZackDitner Offline
Member

Registered: 10/11/02
Posts: 46
Loc: Kitchener, Ontario, Canada
Hmm, usually the ones i install have backup power in each unit.. However, if you think about how you wire interconnected smokies, you use the same gauge wire for the low voltage interconnecting signal

So, I would run another wire of the same gauge and voltage rating, probably a blue or yellow wire, and use it for the backup power, does the backup require both a + & - or just one wire?

I see no code violation as long as all conductors can handle the highest voltage that will be present and conduit fill is considered

Top
#101750 - 02/24/03 01:40 PM Re: exit sign and emergency light hookup?
RobbieD Offline
Member

Registered: 02/23/03
Posts: 238
Loc: Canada
Thanks Zack.

Top
#101751 - 02/25/03 12:22 PM Re: exit sign and emergency light hookup?
wdelbusto Offline
Junior Member

Registered: 02/25/03
Posts: 3
Loc: Miami
Robbie why dont you tell us the model of light you are using it might give you a better under standing. Exit sign come is standard voltages 120v,277v even dual tap (120v/277v) so the circuit will still require one hot and a neutral and a (non-switch) for the EXIT Sign. You mentioned that the light will be Plug I dont think that a plug light is concider for life safety. Think about it if it plug it can be easily unplug and serve no purpose. now when you said plug you meant hardwire?

Regards.

Top
#101752 - 02/25/03 04:13 PM Re: exit sign and emergency light hookup?
CDN_ELECTRICIAN Offline
Member

Registered: 01/22/03
Posts: 75
Loc: Concord,Ontario,Canada
Copy of post in Genaral Forum

In Ontario(If that is where your installation is) you cannot run DC & AC in same raceway.
CSA rule 46-108 (3) "Say's no WAY"

and as iwire noted NEC 700-9 (B),(1),(2),(3),(4)
Basically say's Junction Box attached to fixture (key word "attached),in fixture, and in your case Battery pack.

Top