by ale348 - 03/29/24 01:09 AM
by NORCAL - 03/19/24 05:11 PM
1 members (Scott35), 377 guests, and 17 robots.
The trip values for motor overloads are as per OESC Rule #28-306 . . .
However, if you follow manufacturers instructions, you would be suprised to discover the following:
For Motors with a Service Factor of 1.15
Set the dial setting to the motor nameplate full load amperes.
Then the device trips at 125% of the full load amperes.
For Motors with a Service Factor of 1.00
Set the dial setting to only 90% of the motor nameplate full load amperes.
Then the device trips at 115% of the full load amperes.
Tony Moscioni
Electrical Inspector
Electrical Safety Authority
- - - and for motor starters that require overload heaters to be installed in the field, the heater specified on the instructions are for motors with a Service Factor of 1.15.
For motors with a Service Factor of 1.00 you must install one heater size smaller in order to provide proper protection.
Ed