Looking for a CEC,CBC or CSA code rule that would state the use of #12 wire minimum for lighting in buildings such as hospitals and clinics can find a few rules for commercial buildings like rule 30-104 where the max breaker size may be 20 amp for lighting but nothing that unequivocally states the use of #12.
[This message has been edited by frank (edited 09-30-2002).]
#101671 09/30/02 11:56 AM
Check 24-102(2)
Ed
#101672 09/30/02 12:08 PM
Rule 24-102(2)
Branch circuit conductors shall be copper and shall be sized not smaller than No. 12 AWG.
Rationale for Rule 24-102(2).
We intend that panelboard circuit breakers be inaccessible to patients and other persons not authorized, and consequently this requirement frequently dictates that panelboards be located some distance from their loads. Also, we intend that receptacles at patient care locations be capable of supplying 1000 to 1500 W loads with a reasonably stable voltage.
To satisfy these conditions and the voltage drop requirements of Section 8, we intend that branch circuit conductors be not smaller than No.12 AWG and will frequently have to be larger.
Tony Moscioni
Electrical Inspector
Electrical Safety Authority