#101458 03/20/07 11:15 PM
I'm trying to find a code article that would require a receptacle to serve the countertop of a wet bar located in the family room of a single family home.
George Little
#101459 03/20/07 11:36 PM
George,
If it is a stand alone unit it might fall under island category and it requires one.210-52(C)(2)
If it does not fall under the island category then i would say 210-52 (A)(2)(3) applies.
I like to know what others have to say.
Edward
#101460 03/21/07 01:02 AM
I don't think you will find anything that helps if this is not a kitchen, dining room or bathroom.
AS a design issue this should probably be a dedicated 20 but I fail to see a code requirement for any receptacles at a wet bar.
If they do put one in it has to be GFCI
#101461 03/21/07 07:55 AM
That's what I found too Greg. So if a person wanted to save a few bucks he could forgo the plug over the bar countertop. Save the cost of a GFCI outlet.
George Little
#101462 03/21/07 10:45 AM
Z
I've always gone by 210.52 and it's various sub-sections, in the assumption that the wet-bar will require appliances such as blenders, etc., similar to a kitchen counter top. One circuit is usually acceptable however. GFCI protection on all outlets is definately a must.