Doing a job adding some circcuits for parking lot lights. One of the underground circuits has pvc run to one of those green rectangular underground boxes (with no bottom) and wires spliced in it, in and out. This can't be legal.
The Golden Rule - "The man with the gold makes the rule"
Stay up to Code with the Latest NEC:
>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep
>> 2020 NEC & Related Reference & Study Guides
#101454 03/20/07 01:06 PM
Aldav, this is a common installation and is allowed per 314.30(C)
(C) Handhole Enclosures Without Bottoms Where handhole enclosures without bottoms are installed, all enclosed conductors and any splices or terminations, if present, shall be listed as suitable for wet locations.
Roger
#101455 03/20/07 02:58 PM
Just a thought, does the cover indicate "Electric" ???
The green 'irrigation' don't exactly fly, as they are intended for 'low voltage' circuits.
#101456 03/20/07 04:04 PM
Good catch John, I was thinking Quasite type boxes.