Doing a job adding some circcuits for parking lot lights. One of the underground circuits has pvc run to one of those green rectangular underground boxes (with no bottom) and wires spliced in it, in and out. This can't be legal.
The Golden Rule - "The man with the gold makes the rule"
|
|
|
|
Joined: May 2002
Posts: 1,716
Member
|
Aldav, this is a common installation and is allowed per 314.30(C) (C) Handhole Enclosures Without Bottoms Where handhole enclosures without bottoms are installed, all enclosed conductors and any splices or terminations, if present, shall be listed as suitable for wet locations. Roger
|
|
|
|
Joined: Apr 2002
Posts: 7,381 Likes: 7
Member
|
Just a thought, does the cover indicate "Electric" ??? The green 'irrigation' don't exactly fly, as they are intended for 'low voltage' circuits.
John
John
|
|
|
|
Joined: May 2002
Posts: 1,716
Member
|
Good catch John, I was thinking Quasite type boxes.
Roger
|
|
|
|
Joined: Apr 2002
Posts: 7,381 Likes: 7
Member
|
Roger: I had to read it twice. Thanks for the compliment! John