#101444 03/20/07 08:55 AM
Joined: Mar 2004
Posts: 49
T
Member
Got rejected the other day for useing t-stat class 2 wire. does anyone know where i can find this in the code. this was a residental home wires ran through wood studs thanks

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Aug 2001
Posts: 466
Likes: 1
J
Member
The requirement is for a Class 3 wiring method in the wall. Article 411.4, 2002 Ed.

Joined: Mar 2004
Posts: 49
T
Member
725.61 e (4) says i can use in single family dewling? type CL2 wire is what im useing

Joined: Jan 2004
Posts: 1,507
G
Member
2002 NEC Article 411 Section 411.4 Says you must use the wiring methods of Chapter 3 and CL2 wiring is in Chapter 7. This changes in the '05 a little bit but not completely.


George Little
Joined: Aug 2001
Posts: 466
Likes: 1
J
Member
Read the FPN in Art. 725. " The circuits described hereinare charecterized by usage and electrical power limitations that differtiate them from electric light and power circuit;

You are using the wrong Article. Article 411 is Lighting Systems operating at 30 volt or less.

PS did you even consider the voltage drop using wiring that small? Most LV undercabinet lighting uses 10 Ga.

Joined: Mar 2004
Posts: 49
T
Member
thanks for the info guys

Joined: Jan 2004
Posts: 1,507
G
Member
Quote
You are using the wrong Article. Article 411 is Lighting Systems operating at 30 volt or less.
Jim- Who are you saying is wrong?


George Little
Joined: Aug 2001
Posts: 466
Likes: 1
J
Member
George, I was referring to Tom. Sorry for the confusion.

Joined: Mar 2004
Posts: 49
T
Member
just a quick comment,12 volt lighting system would'nt that fall under 411