0 members (),
390
guests, and
14
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
Joined: Mar 2004
Posts: 49
OP
Member
|
Got rejected the other day for useing t-stat class 2 wire. does anyone know where i can find this in the code. this was a residental home wires ran through wood studs thanks
|
|
|
|
Joined: Aug 2001
Posts: 466 Likes: 1
Member
|
The requirement is for a Class 3 wiring method in the wall. Article 411.4, 2002 Ed.
|
|
|
|
Joined: Mar 2004
Posts: 49
OP
Member
|
725.61 e (4) says i can use in single family dewling? type CL2 wire is what im useing
|
|
|
|
Joined: Jan 2004
Posts: 1,507
Member
|
2002 NEC Article 411 Section 411.4 Says you must use the wiring methods of Chapter 3 and CL2 wiring is in Chapter 7. This changes in the '05 a little bit but not completely.
George Little
|
|
|
|
Joined: Aug 2001
Posts: 466 Likes: 1
Member
|
Read the FPN in Art. 725. " The circuits described hereinare charecterized by usage and electrical power limitations that differtiate them from electric light and power circuit;
You are using the wrong Article. Article 411 is Lighting Systems operating at 30 volt or less.
PS did you even consider the voltage drop using wiring that small? Most LV undercabinet lighting uses 10 Ga.
|
|
|
|
Joined: Mar 2004
Posts: 49
OP
Member
|
|
|
|
|
Joined: Jan 2004
Posts: 1,507
Member
|
You are using the wrong Article. Article 411 is Lighting Systems operating at 30 volt or less. Jim- Who are you saying is wrong?
George Little
|
|
|
|
Joined: Aug 2001
Posts: 466 Likes: 1
Member
|
George, I was referring to Tom. Sorry for the confusion.
|
|
|
|
Joined: Mar 2004
Posts: 49
OP
Member
|
just a quick comment,12 volt lighting system would'nt that fall under 411
|
|
|