Joined: Apr 2002
Posts: 32
S
sudsy4 Offline OP
Member
On the job I'm on, the smoke detectors in the HVAC ducts are powered from the convienience outlets in the RTU's. I don't have a copy of NFPA 72, but this doesn't seem like a good idea to me. Should any one trip or turn off a breaker for these outlets there is an alarm initiated. Any info will be appreciated.


Bill
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Apr 2004
Posts: 156
R
Member
I can't site a specific code but the equipment my company manufactures requires the entire smoke circuit to be operated off of a dedicated fire circuit. That includes the fire/smoke detectors, CO detectors, smoke purge and blower interlocks. If there is an outlet somebody is going to plug a drill into it eventually and depending on the fuse or circuit breaker size pop the circuit.

Edited out CO2 I must have been craving a soda.

Joined: Dec 2003
Posts: 751
E
Member
NFPA 72 requires:

"Fire alarm systems shall be provided with at least two independent and reliable power supplies, one primary and one secondary." and:

"Connections to the light and power service shall be on a dedicated branch circuit." and:

"The OC device shall have a red marking, shall be accessible only to authorized personnel, and shall be identified as 'FIRE ALARM CIRCUIT CONTROL'."


Earl
Joined: Dec 2003
Posts: 751
E
Member
Also, that would be CO detectors, not CO2.


Earl
Joined: Aug 2005
Posts: 214
E
Member
would a CO2 detector be what they use to track gases that cause global warming? j/k

Joined: May 2005
Posts: 984
Likes: 1
G
Member
CO is what they're concerned with; carbon monoxide is much more deadly than carbon dioxide (although they're both bad news in the appropriate concentrations).


Ghost307
Joined: Mar 2007
Posts: 25
M
Member
be sure the power source isn't gfi protected (760.21)