NFPA 72 requires:
"Fire alarm systems shall be provided with at least two independent and reliable power supplies, one primary and one secondary." and:
"Connections to the light and power service shall be on a dedicated branch circuit." and:
"The OC device shall have a red marking, shall be accessible only to authorized personnel, and shall be identified as 'FIRE ALARM CIRCUIT CONTROL'."