#101295 03/05/07 12:28 PM
Joined: May 2002
Posts: 1,716
R
Member
George,
Quote
One hardwires the 70amp device. One does not use a 100amp plug.
why?

We regularly use 100 and 200 amp receptacles for mobile equipment.

Roger

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#101296 03/05/07 12:40 PM
Joined: Nov 2000
Posts: 2,148
R
Member
George,
Quote
One hardwires the 70amp device. One does not use a 100amp plug.
There is a lot of movable or portable equipment that require cord and plug connections. I have installed 400 amp cord connections for a portable rock crushing system.
Don


Don(resqcapt19)
#101297 03/05/07 09:19 PM
Joined: Jul 2004
Posts: 787
L
Member
How about running only two legs of 277/480 plus PE to 3 parrallel 3 phase 50 A pin and sleeve receptacles? All of the devices intended to be plugged in, are single phase welders. I believe the breaker is either a 3 pole 30A or 50A. Commercial establishment.

Larry C

Edit to add last two words.

[This message has been edited by LarryC (edited 03-05-2007).]

#101298 03/08/07 11:34 PM
Joined: Feb 2001
Posts: 308
S
Member
I think it shouldn't happen. I agree that you are inviting overloading of the circuit which is a violation and hazard. If any piece of equipment with a 30 plug is rated over 16 amps 210.23(A)(1) will be violated.

The difference between 10-15amp recepts on a 15 amp circuit and a 30amp recept on a 20 amp circuit is that the likelyhood of the individual piece of equipment being plugged into the 30 amp recept exceeding the circuit rating is greater than the likelyhood that someone will plug in enough stuff to overload the circuit of the 10-15 amps recepts. If the odds were high that 10-15 amp recepts on a 15 amp circuit were overloaded the code wouldn't allow it. Of course in a non-residential setting you wouldn't put 10-15 amp recepts for specific loads on a single circuit if the loads would exceed the rating.

#101299 03/08/07 11:37 PM
Joined: Feb 2001
Posts: 308
S
Member
Don,

What are the odds that someone will plug in a different, higher load, piece of equipment where you installed the plug for the rock crushing equipment? I am assuming probably very low.

#101300 03/08/07 11:43 PM
Joined: Nov 2000
Posts: 2,148
R
Member
Steve,
You are correct that that circuit is not likely to be overloaded. My point was in reply to George's post that said larger circuits should be hard wired. That being said, it should be impossible to overload the conductors of a circuit with an oversize receptacle as the conductor should be protected at or below their ampacity and one of the purposes of the OCPD is to prevent conductor damage from overloads.
Don


Don(resqcapt19)
#101301 03/09/07 02:47 AM
Joined: Jul 2004
Posts: 9,928
Likes: 34
G
Member
George never worked in the computer biz. 60 and 100a 3p Russell Stoll plugs or IEC309s are very common under the floor. Back in the 20th century a decent sized tape drive controller (3803) would have a 100a plug on it. Want to hear the silly thing, they also had 14ga cables going out to the drives protected by the 100a breaker in the machine. I raised hell with IBM about it but they just said U/L listed it. It must be OK.
My worn out old war story about the flaming cable was on this machine.


Greg Fretwell
#101302 03/09/07 12:15 PM
Joined: Mar 2005
Posts: 1,213
S
Member
I've had to hook up equipment that required 25A circuits, but came manufactured complete with special plugs that could only accept a maximum #12 cable. We ended up having to run #10 to boxes behind the rack and use a #12 jumper to connect the equipment.

#101303 03/09/07 05:56 PM
Joined: Feb 2002
Posts: 375
G
Member
While I disagree with others, I allow every professional to do this type of installation as they wish.

I only require that they accept all liability for the installation.

[This message has been edited by George (edited 03-09-2007).]

#101304 03/09/07 07:04 PM
Joined: Mar 2004
Posts: 391
B
BigJohn Offline OP
Member
I appreciate the replies so far. I'm getting a lot on both sides of this argument: Two inspectors told me they wouldn't allow it, but couldn't cite any code off-hand to back up the rejection.

I've brought it up with a lot of experienced journeyman who take Don's position: An overload is impossible because the OCPD will open the circuit and prevent it.

While I agree that overloading the wiring is impossible, I don't read the definition of overload to be limited to wiring or connected appliances:
Quote
Overload.
Operation of equipment in excess of normal, full load rating, or of a conductor in excess of rated amapcity that, when it persists for a sufficient length of time, would cause damage or dangerous overheating. A fault, such as a short circuit or ground fault, is not an overload.
The definition of "equipment" includeds "devices" and a circuit breaker is a device.

George, I'm curious to know, if you are in a professional capacity to restrict this practice, and you disagree with it, what makes you allow it?

-John