Here is something else to read. The manufacture now requires a # 6 bond on all new installations.
http://www.gastite.com/include/languages/english/downloads/pdfs/TB2007_01.pdf

Any inspectors (electrical or plumbing) out there. Is this going to be enforced? Who has jurisdiction?

[This message has been edited by yanici (edited 02-07-2007).]

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Feb 2002
Posts: 114
E
Member
I wouldn't expect bonding done to NEC standards to prevent the high voltage arcing situation on the flex pipe. I'm not seeing exactly how the lightning is coupled to the stove (the vent hood, proximity of stove to lightning bolt, CCC's running over the roof???), but dissipating a high frequency transient with a length of 12 or 14 AWG is hopeless. Even 10 AWG is no good.

Here is a concrete example based on a quick lab test I just did (can't spend too much time on the extracurriculars, but I wanted to post with some hard data). I set up a transient generator for transient with a 2 uS rise and a 10 uS fall to half-crest with an open circuit voltage of 2.5KV and a short circuit current of 500 amps. This may sound like a hefty surge, but it is actually a surge that can be carried, without opening, by a typical 1.25A slo-blo fuse. I discharged this transient into a 12 foot length of 10 AWG wire. I have set up a transient waveform monitor (essentially a high voltage scope probe) to measure the voltage at a point half way along this wire to ground. What I find is about a 800 V bump lasting appr 3 uS at the point 6 ft away from ground (earth and generator return). When I increase the generator current to 2000 amps of potential short circuit current, this bump grows to about 1200 volts and stretches to about 12 uS total. (scope JPGs avail upon request)

This 2000 amp surge is what is coupled to ground from a single 4-wire telecom circuit (clamped to earth) that is expected to survive during GR-1089/NEBS testing. This explains why telecomm equipment manufacturers say to ground equipment using a 6 AWG. Ignore this at your customer's peril (had to throw that in since I know there are some who think the instructions to ground telco stuff with #6 is a bunch of hogwash. It isn't.)

But to the point of the flex pipe... Given the relatively low magnitude of my test, it is easy to see how a really big surge trying to discharge to ground through a much longer run of 14 AWG would develop an even larger potential at the flex pipe. The potential could be, and apparently is, great enough to puncture the jacket and then discharge to plumbing, other conduit, or other grounded objects that are not already carrying the transient current and are therefor still at the true ground potential (as they are not involved in any ground potential rise caused by high freq current through inductive wiring)

My 2 cents.

Joined: Oct 2006
Posts: 745
E
Member
Holy crap, Batman! That's some pretty impressive testing you did to say the least.

I do know of a case where a customer's only gas appliance was a manufactured fireplace which used a metallic stack for a flue. This was the home's only metallic roof penetration and it appears that it was struck by lightning. There was not a hole in the CSST, but there were four spots in the 40 foot pipe run to the propane tank indicating areas for concern. The customer removed the gas option for the fireplace and went back to using wood.

You know............This could be a good thing for electricians when you think about it. Make gas distribution indoors illegal which would mean that the electricians get MUCH more business. I like the idea myself even though it's a "pipe" dream.


---Ed---

"But the guy at Home Depot said it would work."