#100987 01/24/07 06:57 PM
Joined: Jan 2007
Posts: 59
D
Member
Does table 220.19 tell me that if I open up a range and it's stamped 12kw on the inside of door,I can treat it as an 8kw??

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#100988 01/24/07 09:05 PM
Joined: Jan 2004
Posts: 1,507
G
Member
Yes- Absolutely- The text- first paragraph of 220.19. But you should look at the specs and see if they are specifying anything larger.


George Little
#100989 01/25/07 01:03 PM
Joined: Mar 2005
Posts: 1,213
S
Member
Which version of NEC are you referencing? NEC 2005 doesn't have an article 220.19, it skips from 220.18 to 220.40.

220.18(C) allows use of table 220.55 (range/oven demand factor table) for Ranges, is that what you're talking about?

#100990 01/25/07 08:11 PM
Joined: Jan 2007
Posts: 59
D
Member
I'm in the 2002.....Is that table just for your load calculation?