528
14
Can I make up my own extension cord for use on the job? Look at 240.5(B)(3).
George Little
Sure, the NEC doesn't apply to cords that you are using on your job site. It is an installation standard. [90.2(A)]
Ryan Jackson, Salt Lake City
Your right Ryan. For some reason I was remembering the section that used the words "Listed cord sets" and when I did find it, it was "Listed GFCI protection". Must be the CRS kicking in again.
George Little
Posts: 794 Likes: 3
OSHA 1926 subpart K would apply, The wire would need to be 12AWG and the connectors on the ends would need to be rated for use in that application. The practice of making up a 2g box on the end would be unacceptable.
Bryan L. Key Safety Inspector/Trainer Terry's Electric Inc. An Xcelecom Company 600 N. Thacker Ave., Suite A Kissimmee, Florida 34741
BKey, I believe the # 12 minimum is the smallest cord that is allowed to be repaired, I don't think it pertains to making a cord.
If it does can you post the exact section?
Roger