i am running a 1600 amp 120/208 volt 3ph service 300'underground, from a transformer to the building what size parallel wire is needed in alm.(and or in cu.)
Stay up to Code with the Latest NEC:
>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep
>> 2020 NEC & Related Reference & Study Guides
#100046 10/06/06 07:58 PM
Bob Offline
4 #600 cu kcm per phase = 420 x 4 = 1680.
#100047 10/06/06 09:34 PM
Is that 600mcm cu. allowing for the voltage drop in 300'.
#100048 10/07/06 09:08 AM
Duplicate thread, please go to the link below.
https://www.electrical-contractor.net/ubb/Forum1/HTML/007648.html