at a seperate building even if you run a ground with your wiring do you still have to install a ground rod at the seperate building


MAY THE SUN SHINE ON YOUR FACE IN THE MORNING AND YOU AWAKE WITH A SMILE
#101 11/25/00 10:25 PM
Joined: Nov 2000
Posts: 2,148
R
Member
A grounding electrode system is always required at the second building unless it only has one branch circuit feeding it. See 250-32(a)
Don(resqcapt19)