Quote
Is there a specific requirement for bonding to insure the redundant ground path is maintained? Are there specific cable clamps/connectors to be used with this cable?

You must follow the manufactures listing requirments for termination of the cable. With that said most of the time you don't have to do anything with the bond wire but to cut it off or wrap it back over the cable sheath.

As for special connectors, all you need are connectors that are listed for use with AC cable.

Chris