Both EMT and FMC are allowed to be run concealed. I can't believe that the fittings (couplings and connectors) would have to be accessible, even if there is a transition from one raceway type to another.
After reading the commentery in the Handbook, I think 300.15(F) only applies to cable/raceway transitions.