Bill, there is no reason to change a three wire circuit to a four wire if the three wire circuit was compliant when the house was built, and assuming this is the case is the reason they just needed to swap cords with each other.
Just because you might have an older house and buy a new appliance doesn't mean you would have to rewire the house. Note the Exception to 250.140
250.140 Frames of Ranges and Clothes Dryers
Frames of electric ranges, wall-mounted ovens, counter-mounted cooking units, clothes dryers, and outlet or junction boxes that are part of the circuit for these appliances shall be grounded in the manner specified by 250.134 or 250.138.
Exception: For existing branch circuit installations only where an equipment grounding conductor is not present in the outlet or junction box, the frames of electric ranges, wall-mounted ovens, counter-mounted cooking units, clothes dryers, and outlet or junction boxes that are part of the circuit for these appliances shall be permitted to be grounded to the grounded circuit conductor if all the following conditions are met.
(1) The supply circuit is 120/240-volt, single-phase, 3-wire; or 208Y/120-volt derived from a 3-phase, 4-wire, wye-connected system.
(2) The grounded conductor is not smaller than 10 AWG copper or 8 AWG aluminum.
(3) The grounded conductor is insulated, or the grounded conductor is uninsulated and part of a Type SE service-entrance cable and the branch circuit originates at the service equipment.
(4) Grounding contacts of receptacles furnished as part of the equipment are bonded to the equipment.
Roger
[This message has been edited by Roger (edited 06-21-2006).]