This is what we have to follow

Quote
310.15(B)(4)(c) On a 4-wire, 3-phase wye circuit where the major portion of the load consists of nonlinear loads, harmonic currents are present in the neutral conductor; the neutral shall therefore be considered a current-carrying conductor.

How much exactly is the major portion of the load?

50.1%?

75%?

Yes many times some of these circuits are feeding non-linear loads but they also feed linear loads.

Each person will have to decide what is the major portion of load.


Bob Badger
Construction & Maintenance Electrician
Massachusetts