I will give it another shot. [Linked Image]

Quote
250.102(C) Size — Equipment Bonding Jumper on Supply Side of Service. The bonding jumper shall not be smaller than the sizes shown in Table 250.66 for grounding electrode conductors. Where the service-entrance phase conductors are larger than 1100 kcmil copper or 1750 kcmil aluminum, the bonding jumper shall have an area not less than 12½ percent of the area of the largest phase conductor except that, where the phase conductors and the bonding jumper are of different materials (copper or aluminum), the minimum size of the bonding jumper shall be based on the assumed use of phase conductors of the same material as the bonding jumper and with an ampacity equivalent to that of the installed phase conductors. Where the service-entrance conductors are paralleled in two or more raceways or cables, the equipment bonding jumper, where routed with the raceways or cables, shall be run in parallel. The size of the bonding jumper for each raceway or cable shall be based on the size of the service-entrance conductors in each raceway or cable.

The bonding jumper for a grounding electrode conductor raceway or cable armor as covered in 250.64(E) shall be the same size or larger than the required enclosed grounding electrode conductor.

This is how I see it, if you run separated bonding conductors for 'each raceway' each of those conductors will be sized based on just that one raceway.

Quote
The size of the bonding jumper for each raceway or cable shall be based on the size of the service-entrance conductors in each raceway or cable.

However if you daisy chain them nothing changes the bonding jump still has to be based on the size of the service-entrance conductors in each raceway or cable.

Not separately all of them, with them daisy chained you will have count all eight sets of conductors add them up and use that figure with 250.66

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts