Bogger, SE, and USE are cable assemblies, not raceways see the definition of "Raceway" in article 100, and then see the definition of SE and USE in 338.2.

As pointed out by George, the 05 NEC has remedied the confusion of earlier cycles in the xxx.22 sections from 342 through 360 (with the exception of 354).

Note; the cables in 338 are not specifically prohibited from being installed in conduit in that article.

I also agree with Curt and Johns posts concerning the insulation type of the conductors.

Roger