1. The MCC is not the service equipment.

2. The nuetral conductor is not sized to carry a line to neutral fault. That is my issue with this design - what happens to the neutral if there is a line to neutral fault? It seems to me that the neutral conductor could potentially experience major damage during a fault and would have to be replaced. It is to be contained in the same conduit as the line conductors, so I suspect that in the evnet of a line to neutral fault all of the conductors in the conduit would be damaged.

Steve