Plan Review sumittal showed a 800a SUSE rated Transfer switch including overcurrent protection located about 10' from the xformer and generator. The Service point is at the Transfer switch. The building it will be serving is located about 150' away. Question is- What should I expect to see as the Grounding Electrode for the Service?? And, should the contractor run an EGC with the feeder to the building?? There is a water pipe electrode located in the building. Next Question- Do I have to float the neutral??

I don't know if the standard, consisting of metal post and cross members is considered to be a structure.

Your comments are invited [Linked Image]