Depends on the refer.....

Quote
422.10(B) Circuits Supplying Two or More Loads. For branch circuits supplying appliance and other loads, the rating shall be determined in accordance with 210.23.

------------------------------------

210.23 Permissible Loads.
In no case shall the load exceed the branch-circuit ampere rating. An individual branch circuit shall be permitted to supply any load for which it is rated. A branch circuit supplying two or more outlets or receptacles shall supply only the loads specified according to its size as specified in 210.23(A) through (D) and as summarized in 210.24 and Table 210.24.

The requirements of 210.23 are often misunderstood. An individual (single-outlet) branch circuit can supply any load within its rating. On the other side, the load, of course, cannot be greater than the branch-circuit rating.

(A) 15- and 20-Ampere Branch Circuits. A 15- or 20-ampere branch circuit shall be permitted to supply lighting units or other utilization equipment, or a combination of both, and shall comply with 210.23(A)(1) and (A)(2).
Exception: The small appliance branch circuits, laundry branch circuits, and bathroom branch circuits required in a dwelling unit(s) by 210.11(C)(1), (2), and (3) shall supply only the receptacle outlets specified in that section.

Section 210.23(A) permits a 15- or 20-ampere branch circuit for lighting to also supply utilization equipment fastened in place, such as an air conditioner. The equipment load must not exceed 50 percent of the branch-circuit ampere rating (7.5 amperes on a 15-ampere circuit and 10 amperes on a 20-ampere circuit). However, according to 210.52(B), such fastened-in-place equipment is not permitted on the small-appliance branch circuits required in the kitchen, dining room, and so on.

(1) Cord-and-Plug-Connected Equipment. The rating of any one cord-and-plug-connected utilization equipment shall not exceed 80 percent of the branch-circuit ampere rating.
(2) Utilization Equipment Fastened in Place. The total rating of utilization equipment fastened in place, other than luminaires (lighting fixtures), shall not exceed 50 percent of the branch-circuit ampere rating where lighting units, cord-and-plug-connected utilization equipment not fastened in place, or both, are also supplied.
(NEC Commentary in italics)

If the refer is over 7.5A on 15A CT, or 10A on 20A CT, then it is a dedicated circuit for what-ever its rating is......

Quote
422.10(A) Individual Circuits. The rating of an individual branch circuit shall not be less than the marked rating of the appliance or the marked rating of an appliance having combined loads as provided in 422.62.
The rating of an individual branch circuit for motor-operated appliances not having a marked rating shall be in accordance with Part II of Article 430.
The branch-circuit rating for an appliance that is continuously loaded, other than a motor-operated appliance, shall not be less than 125 percent of the marked rating, or not less than 100 percent of the marked rating if the branch-circuit device and its assembly are listed for continuous loading at 100 percent of its rating.
Branch circuits for household cooking appliances shall be permitted to be in accordance with Table 220.19.



[This message has been edited by e57 (edited 02-08-2005).]


Mark Heller
"Well - I oughta....." -Jackie Gleason