Hi,
Are you using raceway or cable?
SE should be protected from the meterbase to the first ocpd if it is subject to physical damage..
Say i run a se cable from the meterbase to the first ocpd, that se cable needs a raceway for PROTECTION.
If you run a SE cable from a meterbase to the first ocpd you really need a disconnect outside. There is NO FUSE between your first ocpd and the transformer! You will need a 4 conductor cable from the first ocpd to your next panel.
Hope that helps.
Regards
greg