If I use the 90 column of 310.16 do the terminal of the OCPD like a breaker have to be rated for AT least the same rating as that of the conductor?

What table do you use most for SE conductors?

I am sizing the conductors for a 200A Service for a commercial job. Can I use 2/0 copper that is from the 90Celcius column?

-regards

Mustang