Quote
2002 NEC 210.52(C)(5)Exception
Exception: To comply with the conditions specified in (a) or (b), receptacle outlets shall be permitted to be mounted not more than 300 mm (12 in.) below the countertop. Receptacles mounted below a countertop in accordance with this exception shall not be located where the countertop extends more than 150 mm (6 in.) beyond its support base.

It seems clear to me, what am I missing?

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts