Yoopersup,
Then I don't agree with your statement. 220.20 only requires that the grounded conductor of a feeder be sized to the maximum unbalanced load. If this maximum unbalanced load exceeds 200 amps, then you only need to size the grounded conductor for 200 amps plus 70% of the unbalanced load greater than 200 amps. If you have a 120/240 volt panel where there is a one 20 amp single pole breaker and ten 2 pole 40 amp breakers for 240 volt loads, the ungrounded conductor could be 500 kcmil and the grounded conductor #12 and be compliant with the rules in the NEC.
Don


Don(resqcapt19)